View the thread, titled "Bs 7288" which is posted in UK Electrical Forum on Electricians Forums.
Jock from the north
Supporter
Without looking in regs have rcd spur units found their way back in book .I've been going through test sheets all day but I'll look after my spag boll.
531.3.4.1 bs7288 only provide additional protection.
There was mention on the forum at the time that they crept back in in the 1st amendment after being missed out in the initial 18th Ed.
It might have even been in a corrigendum (spelling!)
Yeh there def not in initial 18th but are in amm 2 with a note "only provides additional protection" and can be operated by ordinary persons
Well…. What else would you want them to be doing anyway?? By virtue of them being a socket outlet, fault protection is by ADS and over current protection by OCPD already.
These can also be FCU RCDs, which could be used to protect fixed wiring. For what ever reason, these can only be additional protection, and can't be used to meet disconnection times in the way that RCDs to BS61008 etc can be. (although the BS1362 fuse in it could be used to meet disconnection times).