Can I just check, do I multiply the OSG p103 BS3871 M6 Type2 6a by 1.24 to enter on an EIC?
Can I just check, do I multiply the OSG p103 BS3871 M6 Type2 6a by 1.24 to enter on an EIC?
if its only 80% wouldnt it be by 1.20????
I assume you mean to enter in the 'Max Zs' column?
1.25 X will get you slightly closer.
Bs EN 60898 C 10 max Zs = 2.30
80% value = 1.84
1.84 X 1.25 = 2.30