BS3871 Type 2 M6

N

Nicktric

Can I just check, do I multiply the OSG p103 BS3871 M6 Type2 6a by 1.24 to enter on an EIC?
 
I assume you mean to enter in the 'Max Zs' column?

1.25 X will get you slightly closer.

Thanks that what I expected then noticed on page 100 OSG it refers to correction factor 1.24.. curious or is this something else all together!?

Also I was testing today and did a Zs on lighting at the max r1 + r2 and did a couple of random Zs on other points, I got a higher Zs on a point with a lower r1 r2 reading than the point with max r1 r2 if that makes sense?! Only marginally but is there a logical reason for this or have I just missed something?
 