afternoon
first time since amendment 3 came out that I have had to install a TT system
I need to install site temps on a plot of land ready for new build flats.
UKPN will be installing a new PME temp supply
Am I right in thinking I am ok to take my tails through a nylon Wiska tail gland- through a amendment 3 board using a clamp. with a 100ma timed delay main switch.
then 30ma RCBO any of the circuits out of here that need them. think they are getting site cabins with pre wired boards in them anyway.
Cheers