OP carl9254 - Joined Oct 3, 2009 Messages 201 Reaction score 0 Dec 3, 2009 #16 I get 6.525, so 10mm would be good, thanks for that so this equation is used to determine earth size from met to cu?? Ill do the job tomoz.
I get 6.525, so 10mm would be good, thanks for that so this equation is used to determine earth size from met to cu?? Ill do the job tomoz.
OP carl9254 - Joined Oct 3, 2009 Messages 201 Reaction score 0 Dec 3, 2009 #18 So the k reading would generally be 115?? Because housing cable is copper pvc 70 deg?? So if i wanted to work out this for my downstairs sockets circuit for example where would i stick my probes for the I reading??
So the k reading would generally be 115?? Because housing cable is copper pvc 70 deg?? So if i wanted to work out this for my downstairs sockets circuit for example where would i stick my probes for the I reading??
G Guest123 Dec 3, 2009 #19 You wouldn't need to. Fault current (I) = Uo/Zs So 230V/the Zs for that circuit = your fault current.
You wouldn't need to. Fault current (I) = Uo/Zs So 230V/the Zs for that circuit = your fault current.