i see. so there's no hard and fast rule that a FCU has to be fitted when the distance between the fixed equipment and the CCU is so small that the CB can reasonably be used as the local isolation. Some people would go 6 amp CB to 3 amp FCU to alarm. others would track down a 3 amp CB and go straight to the alarm.

would it be especially bad practice to go from a 6 amp CB straight to the alarm?
 
Let's not forget the basics regarding fuses.

The fuse/mcb is there to protect the cable. Most alarms are fed from a socket circuit. The alarm only needs 1mm cable so the mcb is over rated for the spur 1mm cable. In this case a fcu needs to be fitted to protect the 1mm cable therefore a 3A or 5A fuse to be used.

If your feeding it from the cu you can use a 3A or 6A mcb without the use of a fcu.

If the alarm panel was on its own dedicated circuit but no where near the cu I would always fit a fcu close to the panel for safe isolation for maintenance/repair.
 
An mcb can be used as a local isolation device long as its within "reasonable" distance and can be locked off. You can also use a mcb for functional switching.

In your case if the alarm is the only thing being fed from this circuit you don't need a fcu. Clearly mark the cu, alarm do not switch off. Please don't do what I've seen in domestic and commercial installs and put a bit of lecy tape over the mcb switch. Not good if it needs to trip!

Yep you can do this but sometimes an alarm is an afterthought and is doubled up with a lighting circuit ie 6 amps also does not help if the lighting circuits has a couple of strip or GU10 lamps on them.
 

Reply to burglar alarm feed question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
184
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Suggestions for best place to find suitable installers to quote?
Replies
4
Views
363
  • Question
Personally, I would take a Ze measurement myself rather than rely on someone else's maybe drive by scrap of paper.
2 3
Replies
31
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top