Hi all
Just checked job and 6mm live supply is burnt out on 8.5kw shower. Run is 4 metres clipped direct with no insulation my calcs are that this should be perfectly fine. Was also on a 40 amp wylex push type mcb. Terminations seemed fine. Has anyone got any possibilities what may be causing this? I was also getting 115v across disconnected live feed and load neutral. My understanding is that this can be normal but can someone clear up the theory behind this. Thanks
Just checked job and 6mm live supply is burnt out on 8.5kw shower. Run is 4 metres clipped direct with no insulation my calcs are that this should be perfectly fine. Was also on a 40 amp wylex push type mcb. Terminations seemed fine. Has anyone got any possibilities what may be causing this? I was also getting 115v across disconnected live feed and load neutral. My understanding is that this can be normal but can someone clear up the theory behind this. Thanks