Been doing some work today at a site and the 2 electricians that work at the place are putting in a new. Busbar Chamber for some machines.
They have come from the main switch with some 70mm swa into a Fused switch and into the chamber with some 70mm TRI rated. All looks good. I then notice the fisrt set of cables they have taken off into a 63Amp switch fuse are only 25mm off the bus bar. Now I am missing something here as when ever I have done one I have used the same size cable to every out going switch as the cable must be rated to 160amp?? :tounge_smile:
 
Now I am missing something here as when ever I have done one I have used the same size cable to every out going switch as the cable must be rated to 160amp?? :tounge_smile:
So how would you get 70mm2 cables into a 20 amp red Fire alarm switch fuse then? they are quite commonly bolted onto Busbar Chambers, you may well break the guinness book of records if you can manage that.
 
Was hoping you could explain your comment in post 1 regarding the fact you said and I quote "when ever I have done one I have used the same size cable to every out going switch as the cable must be rated to 160amp??" Seems kind of strange IMO, as the majority of switch fuses under 160 amps will be difficult to get 70mm2 tails in, Even a 100 amp switch fuse can be awkward with 50mm2 tails, unless it takes lugs rather than has connector pots, so a 63 would be impossible, was hoping for some clarification from you fella.
 
Sorry in Isle of Man getting ready for this years TT so not been on here.
I must be getting confused then its been a while since i did any bus car chambers. And can never remember fitting any thing less than 100amp stuff on to them. I was just thinking about the short or fault current on the cable. But guess over such a short cable run it will be fine.
 

Reply to Bus Bar Chamber in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
362
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
328
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
371

Similar threads

Busbar chambers are often considered what's often termed as 'fault free zones' as per BS EN 61439 where firstly the primary purpose of protection...
Replies
2
Views
1K
  • Question
Assuming you are a novice to electrics? As in no access to electrical equipment. Plug something in to the sockets that you know works else where...
Replies
1
Views
365
Cbelectrics
C

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top