Been doing some work today at a site and the 2 electricians that work at the place are putting in a new. Busbar Chamber for some machines.
They have come from the main switch with some 70mm swa into a Fused switch and into the chamber with some 70mm TRI rated. All looks good. I then notice the fisrt set of cables they have taken off into a 63Amp switch fuse are only 25mm off the bus bar. Now I am missing something here as when ever I have done one I have used the same size cable to every out going switch as the cable must be rated to 160amp?? :tounge_smile:
They have come from the main switch with some 70mm swa into a Fused switch and into the chamber with some 70mm TRI rated. All looks good. I then notice the fisrt set of cables they have taken off into a 63Amp switch fuse are only 25mm off the bus bar. Now I am missing something here as when ever I have done one I have used the same size cable to every out going switch as the cable must be rated to 160amp?? :tounge_smile: