Yeah i understand the 63amp BS88 fuse can only demand 63amps, but what happens in the case of the cable supplying the 63amp switch fuse shorts out?

Thanks

If you understand how a '63A BS88 fuse can only demand 63A', perhaps you be kind enough to enlighten myself and the masses on here, because I fail to see how what is effectively a fusible conductor of negligible impedance limits the current to just 63A. Contrary to your 'understanding' I know that a BS88-6 fuse, for example, has a short circuit capacity of 80,000A@415V.
 
Hi Markie,

I know that a BS88-6 fuse, for example, has a short circuit capacity of 80,000A@415V

Isn't this the maximum prospective fault current for this device ? or is this the Icn, the absolute maximum fault current this device can clear ?

The 63 A part is the In or nominal trip rating, and this is time dependent, in this case APP 3(fig 3.3B) BRB, would pull 400 A for 1 sec and 280 A for 5 secs before clearing the fault.
 
Last edited:
Ah! Thanks Malcom, The cable, which is a reduction (in relation to the bars) should have been 3 M or less, or the protective device (63A) should have been within 3 M of the bars, I had a look at the original post

Also we don't know if the circuit only provides overload protection only, or short circuit protection only
 
Last edited:
There are standards (BS 159) for busbars, busbars may operate above the 70 C so cables and terminations need to be considered.

433.2 allows us to position the protective device along the conductor providing that certain requirements are met. I we use (i) of 433.2.2 then we need to povide fault current protection to the 10mm cable.

So we need to consider the I2T in relation to K2S2.

Chris
 
Hi Chris,

There are standards (BS 159) for busbars, busbars may operate above the 70 C so cables and terminations need to be considered

This is probably one of the reasons why the panel builders I worked for insisted on DI cables, as these were rated IIRC @ 90 degrees or higher, and had a higher CCC than both PVC and LSF for an equivalent csa (we were issued with CCC cards).

Ps. I wasn't a designer, just a cable monkey :stooge_moe:
 
Last edited:
There a few standards with give guidance on busbar temps, IEC 439,BS EN 60439-1, BS 159, there is guidance within these documents on how to terminate cables which have a limiting temp of 70 C, though most would go for a cable which is suitably rated.

Chris
 
The applicable regs are 433.2.22 and 434.2.1.

The cables must be less than 3 mts long. And must have enhanced fire and personnel protection eg steel containment and in a normally unoccupied area.
 

Reply to Bus Bar Regs? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
605
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top