Hello People

Currently within a carpentry workshop the old main 200a 3 phase isolator needs replacing which currently supplies an equity as old main busbar chamber and in doing so i have to replace some old VIR main tails. (complete birds nest)

I am not sure on the best way to connect my mains tails to the old busbar (35mm wide), i am going to be using TR750 50mm tri rated singles cabling for the supply between the new isolator and busbar, i have attached images of how the old tails are connected and my initial thinking is how can i get a nice connection onto the aluminium busbar?
 

Attachments

  • [ElectriciansForums.net] Busbar connections
    p2.jpg
    88 KB · Views: 65
  • [ElectriciansForums.net] Busbar connections
    p1.jpg
    96.1 KB · Views: 57
Can you drill and tap the bus bar and bolt connect a crimped eye to it?
 
They'll be Tinned copper.
The "Lugs" for the VIR look like they maybe a well engineered, given it's age, clamp.
It's an angle bracket with the end threads of a bolt showing.
It may be there's a lug on the bottom of the bracket or it may just clamp the bare end of cable.
At worst it would mean unbolting the bracket and bolt a lug on in it's place with the new 50mm Tri in.
 
It'd be interesting to know what some of those smaller cables are feeding and how far they are travelling, being on a 200amp supply.
It just looks like a 3 phase pick up point.
 
They'll be Tinned copper.
The "Lugs" for the VIR look like they maybe a well engineered, given it's age, clamp.
It's an angle bracket with the end threads of a bolt showing.
It may be there's a lug on the bottom of the bracket or it may just clamp the bare end of cable.
At worst it would mean unbolting the bracket and bolt a lug on in it's place with the new 50mm Tri in.
thank you for the response, what nut and bolt set up would give the best contact and should i use spring washers or anti slip washers?
 
They'll be Tinned copper.
The "Lugs" for the VIR look like they maybe a well engineered, given it's age, clamp.
It's an angle bracket with the end threads of a bolt showing.
It may be there's a lug on the bottom of the bracket or it may just clamp the bare end of cable.
At worst it would mean unbolting the bracket and bolt a lug on in it's place with the new 50mm Tri in.
thank you for the response, what nut and bolt set up would give the best contact and should i use spring washers or anti slip washers?
 

Reply to Busbar connections in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
My thoughts exactly! Snowed under with work at the moment, so might have to pass it on 😬😬
Replies
4
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
884

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top