hi guys,

i'm working on "kitchen rescue" after watching gordon ramsey's "kitchen nightmares" (season 2, episode 5)... where a fairly young owner turns round a failing restaurant (that hadn't been cleaned since she bought it 5 years ago) ?

since we're in plague times and my kitchen was become an insect cemetery, i took the approach of sucking up the carcasses with my vac: a fairly cheap tesco model: VCBL1441, 220V-240V, 1400 Watt.

while using vac in hallway socket, I heard a constant buzz from socket, so switched if off immediately... I note on bottom right side of socket, it has trademark "tenby". Now, i have electrical knowledge, but I'm not a trained sparks... Do I:

1. fit a new socket (and hope for the best)?
2. call in a qualified sparks to trace the fault?
3. call my landlord (its a rented property) and let them sort it?

its a flat I'm in, fitted with a new consumer unit, (not sure if I have new color wiring)... running UK power supply (230V AC).
thoughts welcome.

regards nb
 
If it's an ordinary switch socket, with no USB outlets, then the buzzing is probably an AC arc, either from a loose connection to a wire, or a faulty switch.
Either way, a new socket should cure it, although a heat damaged wire might cause complications.
 
hi guys,

thanks for great feedback...? my landlord (god bless 'em) is a council, so has the reaction speeds of a banker being asked to donate at a fundraiser.... ? but yeh, an arc somewhere in the socket or wiring to it sounds highly likely

i did actually work with a pro-sparks who came out and checked all the terminations in (most) sockets (he replaced a faulty socket in the kitchen, too)... it's not his fault, these things just happen over time...

its a bit beyond me to change out mains sockets... (and as brian points out) it could be a wiring issue to the socket... so, yeh... i'll see what my landlord advises first (that will be interesting)... ?

i'll keep a log of events (as is my habit) for forum members amusement (heh, heh)

thanks again, nb
 
just for academic purposes.... ?

theres a few "tutorial" videos about replacing mains sockets on youtube (that peeked my interest).... i know it's a kind of bread and butter job for most pro-sparks... some vids ...well first 2 i reviewed weren't pros. then I came across andys vid (he's obviously a pro sparks).

he didnt re-terminate the wires going into the socket plate, but I noticed he had "chucky terminations" (plenty of copper terminator) and ensured no bare copper wire was showing... so less chance of arcing, right?

he doesnt use any fancy multimeter to test circuit is dead, but instead, a simple "socket tester" that stops beeping, once he's terminated power to that socket circuit... and has an interesting tape technique to ensure CU switch doesn't spring back to live ... (or get turned on by someone else)!

he mentions the "oldskool" wiring too (which most amateurs wont consider). i found a pic of the color codes (for anyone interested).

his enthusiasm and amusing "advertising" technique at the end of the vid gives me confidence to attempt this repair, but i lack two things...

1. a socket tester
2. knowledge of the best "replacement socket" to buy...

i dont know if I can advertise individual electricians here, or even if I can post youtube links, so (hopefully) someone can let me know... ?

kind regards, nb.
 

Attachments

  • [ElectriciansForums.net] Buzzing Mains Socket
    WiringColorsUK.jpg
    24.4 KB · Views: 31
Rule number1. Safe Isolation. Rule number 2. Safe Isolation. Rule number 3. Safe isolation before even thinking of doing anything with your electrics. Check with landlord first but you can’t go wrong with videos by GSH Electrical as they teach apprentices. Likely a loose connection or faulty contact in the socket that is a quick job to replace.
 
As above, check with the landlord first as they may well have a policy of only certified electricians doing any work at all.

If you do plan on trying it yourself then you MUST ENSURE IT IS DEAD first, or you might well end up so. Simply turning off the whole flat's power is usually enough, but we have heard of cases where a house was divided up and the odd socket was actually powered from another's flats supply. So test it somehow to (1) show your socket tester sees power when on, then (2) tester goes dead with all of the flat off, and (3) make sure nobody else is going to switch it back on until you are safely done

Take a photo of the old socket before you disconnect anything.

Make sure the wires are serviceable before doing any more, so long enough to work with and not showing signs of charred insulation. If in doubt post you photo here for advice.

You might need to strip the ends to have clean wire if it has been arc-damaged, so you need significant skill with a cutter or best of all get a proper wire stripping tool.

Put in a decent brand of socket, such as MK Logic range (not base/essentials, they are crap) or the likes of Schneider, Click Scolmore, etc. Check which hole is which with good light (so L, N and E) before you try to get the cables in.

Finally check it with your socket tests on completion to make sure you don't have L/N swapped or similar.
 
When reporting it to the council did you mention the fire risk? To be honest, if there is arcing in the socket you should be isolating the circuit straight away and getting it fixed before re energising.
 
So test it somehow to (1) show your socket tester sees power when on, then (2) tester goes dead with all of the flat off, and (3) make sure nobody else is going to switch it back on until you are safely done
Forgive me for being totally pedantic…
4) try the socket tester in another circuit, like the plug on a cooker switch, to prove it didn’t randomly stop working at the wrong moment

EDIT just saw you said main switch, fair enough

Btw Screwfix sell a lock off kit and a cheap 2 pole tester which are handy things to have around.
 
Forgive me for being totally pedantic…
4) try the socket tester in another circuit, like the plug on a cooker switch, to prove it didn’t randomly stop working at the wrong moment

EDIT just saw you said main switch, fair enough
No problem. Generally I would not suggest locking off just the one circuit to a DIY person unless they really have enough skill and a suitable tester to make sure it is dead and no reversed polarity risk. At which point they probably are not "DIY"!
Btw Screwfix sell a lock off kit and a cheap 2 pole tester which are handy things to have around.
Yes, always good to see stuff like that. My own preference are for the simple voltage testers without battery as less risk of needing it again in a few years trashed by a leaked battery.
 
Just looked again, this is just the ticket:
 
Just looked again, this is just the ticket:
Yes, that’s the one I had in mind. Only question is whether it has probe caps. However they state it meets GS38 standards in the answer to a question.
 
Yes, that’s the one I had in mind. Only question is whether it has probe caps. However they state it meets GS38 standards in the answer to a question.
Ah a review says “Excellent two pole tester. Very well made, and supplied with GS38 compliant removable tip covers which are not evident in the catalogue picture”
It does indeed look just the ticket.
 

Reply to Buzzing Mains Socket in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
846
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
968

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top