Al-42

I have a 500W Security light with a built-in PIR sensor.
See: https://www.amazon.co.uk/gp/product/B005OB0MVW/

It works fine, but if I'm outside at night I have to move within range every few minutes to keep it on.
So what I want to do is fit a switch to bypass the PIR.

The four-way terminal strip has:
(1) live - goes to live of the PIR.
(2) Neutral - goes to neutral of both the PIR and the light bulb.
(3) Earth - goes to casing.
(4) The switched live from the PIR connects to the light bulb.

upload_2016-11-11_11-50-50.png

What I would like to do is fit a small weatherproof box close to the lamp with a five-way terminal strip, and run a three core down to a weatherproof single-pole double-throw switch. This could then be wired so that the switch either connects the live to terminal (1) and the light works as per normal, or, when switched the other way connects the live to terminal (4) keeping the light on.

upload_2016-11-11_11-52-27.png

My question is - since doing this will also connect the live to the switched live from the PIR, will this damage the PIR sensor?

upload_2016-11-11_11-50-1.png
 
As an Amazon Associate we earn from qualifying purchases.
That is the way to do it.

But 500watts? blimey, think about the planet.
Instead, go buy a 20watt LED PIR flood and save the polar bears (and your energy bills!)
Get one with a pulse over-ride feature, then you won't even need the switch!
 
There should be no need to switch the supply to the PIR. Just connect the switch between permanent live and switched live. That way the PIR won't have to do whatever it does when first powered up every time you switch back to 'auto'.
 
There should be no need to switch the supply to the PIR. Just connect the switch between permanent live and switched live. That way the PIR won't have to do whatever it does when first powered up every time you switch back to 'auto'.

And also by switching the pemanent live it could stay on all the time
 
There should be no need to switch the supply to the PIR. Just connect the switch between permanent live and switched live. That way the PIR won't have to do whatever it does when first powered up every time you switch back to 'auto'.

Thanks very much for that. Sounds like a much more elegant solution. It also means I can get away with using a single-pole single-throw switch.
 
This is why its a good idea to run 3C&E to outside lights... from the internal switch!

Agreed, but it's an old house and I'd have to do a load of drilling and tracking to fit a switch indoors, so that's not an option.

Back to the subject of wiring - it occurs to me that it would be ideal to use a three-position switch (off/PIR/on) but I've been unable to find a weatherproof 3-pos switch on-line. I've looked in all the usual places (Wickes, Screwfix etc.) but with no success. Does anyone know where I could find such a thing?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Bypassing a PIR sensor
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
Al-42,
Last reply from
Al-42,
Replies
8
Views
21,908

Advert

Back
Top