How sad am I! Here in Scotland on New Year's eve I'm wading my way through the theory of "Testing Continuity of Protective Conductors" - Method 2 (Long Lead) from the C&G Level 2 Textbook on page 384.
The question is:
"The resistance of a long lead is measured at 0.89 ohms. The low-resistance meter gives a reading of 1.63 ohms. What will the value of R2 be?"
The answer given is given as 0.9 Mega Ohms. Surely this is wrong or am I missing something?
 
Last edited:
Way off. What do we measure in Mohms?

The question is a lot easier than you think.
 
Yep, the answer given ( in your book) appears to be wrong.
It appears to suggest that the resistance of the long lead itself has not been removed from the measurement by zeroing the leads.
So answer should probably be 1.63 - 0.89 ohms.
 
Thank you all very much for your replies...especially on New Year's eve. To give an answer to Strima's question - we measure insulation resistance in Mega Ohms. I figured the answer to the question resistance should be the difference between the reading given for the protective conductor and the resistance of the long leads. Wouldn't you normally just "null" the leads? In any case, I'm disappointed that the book has published the wrong answer (image of the answer attached) Should we let them know?
[ElectriciansForums.net] C&G Level 2 Diploma Query
 
Let them know that the answer is wrong.

So what is the correct answer?
 

Reply to C&G Level 2 Diploma Query in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
980
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It was a one time ÂŁ19.99 fee. I'll be reaching out to them though to get that back. It was the only online extensive bank of questions that I...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top