I have quoted for a job of fitting a CT chamber and doing the intake alterations to change a 100A 3-ph supply to 200A 3-ph and in doing so obtained a price for the CT Chamber from Ryefield. The metering company need to know the CT ratio to complete their form so they can book the job, so the client asked me for this info. I got on to Ryefield who said that they dont supply the CT coils ??? and as far as I remember from last time I installed one they came in the chamber already, so now i'm trying to get an answer while Ryefield have finished for the week at 2PM and no-where on-line can I find a decent pdf of the kit to look at ................. help :eek:
 
As far as i recall a standad meter kw/h requires a a current between 0 to 5A so if you had a 200amp supply i believe you need a ratio of 200/5, the 200 is proportional to your current you are measuring and the 5 is a standard secondary current for the meter.

Thus a 100amp supply would need c.t.s with a 100/5 ratio etc

I think this is how it works when choosing your c.t.s but be best to look up some c.t.s in a catalogue and ring tech for advice which is only the cost of a phonecall, they are always happy to help and this is how i learn alot of things college never taught me.

Note you will probably have to price for a c.t. per phase
 
Last edited by a moderator:
cheers, that helps, but Ryefield are an old firm that finishes early on a friday and I seem to remember ringing 'during their lunch hour' once too ;-( so their technical probably wont be around until Monday midday after tiffin and jam sandwiches. :D
 
I installed a 600A Ryefield ct chamber a little while back, CT's were supplied by the metering co.
Scottish & Southern I believe.
 
Please be aware you need to specify metering CTs as these are different from protection CTS , also the supply authority will require a certain class of CT ( 0.5M) ( 0.1M) etc
 
Please be aware you need to specify metering CTs as these are different from protection CTS , also the supply authority will require a certain class of CT ( 0.5M) ( 0.1M) etc
I do hope he's sorted this out by now as its nearly 4 yrs old since this thread was posted but you could be lucky as he might still be waiting in a queue for technical support......... You are no3 in the queue ....we will be with you shortly!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

stretchyboy

Arms
-
Joined
Location
Hertford
Website
http://imelectrical.com/
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
I M Electrical Contracts Ltd

Thread Information

Title
C T Ratio
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
9

Thread Tags

Advert

Thread statistics

Created
stretchyboy,
Last reply from
brookster,
Replies
9
Views
12,111

Advert

Back
Top