Please help, just had a domestic EICR undertaken, a C2 issue: Consumer Unit does not meet minimum I.P rating, what does this mean and how do I check this out? how expensive to rectify? thanks!
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss C2 issues? Consumer Unit & Circuit forms a Figure of 8 Rather than a complete RFC? in the UK Electrical Forum area at ElectriciansForums.net
No, you would need to ask the electrician who did the inspection for some detail on that.Is there any way of telling from the EICR report?
I get the feeling I'm being a bit ripped off, particularly as I think they were lining me up to buy a new CU. What would I be able to go back with so I sound a bit more clued up?No, you would need to ask the electrician who did the inspection for some detail on that.
Given they have said circuit 6 presumably it is a single MCB involved so closer to @westward10 comment.
I guess that would cause the circuit to trip out more than usual?It is still not good for several reasons, one is you can't perform the usual RFC end-end checks and get all/most sockets connections verified that way.
Other point is unless you know where the loops touch you could end up with a lot more of the current on one leg of the circuit so potentially overloading the cable as the RFC typically uses 2.5mm cable rated at 20A (or so, depending on the installation method) but protected by 30A fuse or 32A MCB on the assumption of moderately sane load distribution.
Fixing the circuit is best answer, but if in doubt dropping the MCB to 20A at least removes the risk of cable overload.
Are you based in S Wales also?I see you're in Swansea... is the property also in Swansea?
Without seeing it we can't tell.I get the feeling I'm being a bit ripped off, particularly as I think they were lining me up to buy a new CU. What would I be able to go back with so I sound a bit more clued up?
Does it usually trip?I guess that would cause the circuit to trip out more than usual?
I think that is the answer then, drop the MCB to 20 ADoes it usually trip?
Unless you have all of the kitchen and rest of the house with heaters, etc, on the same RFC then you are unlikely to trip the MCB on over current at 20A. However, if it is the RCD that is tripping due to a selection of leaky electronics then the better solution would be a new CU with all RCBO so you don't have several circuits accumulation leakage to the point a common RCD trips.
Are you based in S Wales also?
It might be a solution but you still need to check all of the sockets are soundly connected. I suspect the 'FI' code is down to being unable to verify they are OK in the usual end-end test.I think that is the answer then, drop the MCB to 20 A
You ignore the 50mph through Port Talbot it is half an hour awayYes, but I operate in/around Cardiff and Newport.
If you haven't already then ask for a detailed quote for the remedial works. The C2s are the only ones you must correct - the others are optional.I get the feeling I'm being a bit ripped off, particularly as I think they were lining me up to buy a new CU. What would I be able to go back with so I sound a bit more clued up?
Thank you, yes the CU is 7 years old approx and it is a small house, just three bedroom terrace. Sockets number around 10 throughout the whole property I think.If you haven't already then ask for a detailed quote for the remedial works. The C2s are the only ones you must correct - the others are optional.
You are also at liberty to get other quotes for the work - there is no requirement in law to get another report that says 'satisfactory' on it - just to correct the issues that were discovered.
It does make it easier with letting agents to have the one satisfactory report, but all you need by law (assuming this is a let property) is the EICR plus proof that all remedial works have been completed.
The Figure of 8 issue probably needs some more detailed investigation - however, from the looks of the consumer unit I'm guessing it's not a huge property so unlikely to be a lot of sockets?
If the 'alteration' they mention has been made at a socket it may well be easy to resolve. If not, and the sockets don't cover lots of appliances or kitchen, then dropping it to a 20A radial may well be the easiest/cheapest solution.
The consumer unit would appear to be one that was installed within the last 10 years or so - was there any documentation/certification with it, as that may reveal whether the original installer or the current tester has done a better job?
It sounds like the two moved sockets would be a good candidate to start investigating then!Thank you, yes the CU is 7 years old approx and it is a small house, just three bedroom terrace. Sockets number around 10 throughout the whole property I think.
Downstairs recently there was a 'false wall' put in which sits 2 inches in front on the old wall, two sockets had to be moved, now one doesn't work.
I think the sockets do cover the kitchen, but not entirely sure. I'll try and get a picture of the CU tomorrow.
So by law I guess I do have to have a competent person undertake the FI too
Reply to C2 issues? Consumer Unit & Circuit forms a Figure of 8 Rather than a complete RFC? in the UK Electrical Forum area at ElectriciansForums.net