How is a spur off a Ring final circuit wired in 4mm twin and earth a C2 observation? How is it likely to become dangerous? Has the tester inspector provided any reasoning?
An EICR is checking for compliance to BS7671, not coding because it’s unusual, or “I wouldn’t have done it that way”! In my opinion any coding needs to be backed up by at least one regulation from the wiring regs that it is breaching. Not just an opinion that it is wrong.
Is it due to the terminations of both 4mm stranded and 2.5mm solid conductors into the terminals of a BS1363 accessory? In which case I may tend to agree this MAY breach 526.2 among other regs.
4mm T&E in its self on a ring in my opinion doesn’t breach any regs. 433.1.204 states RFC must be wired in AT LEAST 2.5mm copper conductors with AT LEAST 20a Iz (except micc). So 4mm T&E complies.
Recently I have come across a fair amount of coding which are at best a bit weak and at worst blatant fishing for work. Coding such as “C2 requires metal fuse box upgrade - plastic dangerous”. “C2 kitchen light not waterproof”.
I’m not sure how others who have been asked to do remedial works overcome this. Most individuals I haves spoken to are not likely to get another full EICR? (As it’s likely just a paper exercise for their letting agency).
I have sometimes retested the circuit in question (As in my opinion any one who has done this won’t have tested properly). And then issue a minor works for the circuit stating test values and regulations as to why it is compliant with the regs. This way the customer can keep the MWC as they would if any actual remedial work had been carried out.