What is the proper way to size this up.
7.5 kw 3 phase + n motor in a dry cleaning machine.
Is it 7500/400x1.732= 10.82 amps per phase
= 2.5 mm2 in trunking method 3, 21amps current carrying capacity
Do i have to oversize the cable for inrush current? Or is 2.5 ok?
Thanks.
 
calculation is good .

You need to take length of run into account . Don't have regs to hand but depending on length of run and reference method i would have thought 1.5mm would suffice ...

You need to take inrush current into account for sizing the type of over current device not cable size . The inrush will be over a short period of time .
 
2.5mm is OTT. 1.5mm is the appropriate size unless volt drop is excessive.
 
Is the 7.5Kw the max demand of the dry cleaner or the rating of the motor? Your opening post is a bit unclear.
 
Thanks lads the run is 27 meters, 16 amp type c be ok. On 2.5
1.5 ccc is 11.5 amps mcb sizing would be a problem couldnt put 10 amp mcb if flc is10.8 per phase?
 
TP and N motor?

You need to use the various factors in your calculation, not just jump straight to the tables. Also you don't appear to have included power factor or motor efficiency in you calculation.
With motors you do need to ensure the supply mcbs is big enough to avoid nuisance tripping on startup.

You are only providing fault protection with the MCB as the motor overload will handle overload protection,
 
Thanks lads the run is 27 meters, 16 amp type c be ok. On 2.5
1.5 ccc is 11.5 amps mcb sizing would be a problem couldnt put 10 amp mcb if flc is10.8 per phase?

Without clarifying the info I requested then we cannot answer your query, like has been said - machines with motors need careful consideration and circuit design to ensure you don't end up with nuisance tripping, motors size is crucial here unless the installation instructions specify front end device.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Cable and mcb sizing
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
10

Thread Tags

Advert

Thread statistics

Created
pierce,
Last reply from
benji,
Replies
10
Views
5,250

Advert

Back
Top