What is the proper way to size this up.
7.5 kw 3 phase + n motor in a dry cleaning machine.
Is it 7500/400x1.732= 10.82 amps per phase
= 2.5 mm2 in trunking method 3, 21amps current carrying capacity
Do i have to oversize the cable for inrush current? Or is 2.5 ok?
Thanks.
 
calculation is good .

You need to take length of run into account . Don't have regs to hand but depending on length of run and reference method i would have thought 1.5mm would suffice ...

You need to take inrush current into account for sizing the type of over current device not cable size . The inrush will be over a short period of time .
 
Thanks lads the run is 27 meters, 16 amp type c be ok. On 2.5
1.5 ccc is 11.5 amps mcb sizing would be a problem couldnt put 10 amp mcb if flc is10.8 per phase?
 
TP and N motor?

You need to use the various factors in your calculation, not just jump straight to the tables. Also you don't appear to have included power factor or motor efficiency in you calculation.
With motors you do need to ensure the supply mcbs is big enough to avoid nuisance tripping on startup.

You are only providing fault protection with the MCB as the motor overload will handle overload protection,
 
Thanks lads the run is 27 meters, 16 amp type c be ok. On 2.5
1.5 ccc is 11.5 amps mcb sizing would be a problem couldnt put 10 amp mcb if flc is10.8 per phase?

Without clarifying the info I requested then we cannot answer your query, like has been said - machines with motors need careful consideration and circuit design to ensure you don't end up with nuisance tripping, motors size is crucial here unless the installation instructions specify front end device.
 

Reply to Cable and mcb sizing in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that...
2
Replies
29
Views
2K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top