chloebear

I have a site where a large number of circuits were rewired about 4 years ago in LSF twin/earth. these circuits include lighting, showers, sockets etc - all fairly standard stuff on the face of it.
Problems have developed over the last 6 months with cable burn-out on certain accessories - 2x light fittings have burnt out the fittings at the terminals, a shower isolator (50amp) has burnt out & a fan heater has caused fairly serious fire.

Seems too random for poor workmanship - I am now starting to think along the lines of sub standard cable.

anyone out there come across this as an issue & what would be he best way to test for this?????
 
Why?
Bolted terminals have worked perfectly well for decades, if you tighten them properly there should be no issues. OK, the cheap cack has rubbish bolts but as long as you use a decent brand you'll be fine?
I think your idea will be used as an excuse for poor workmanship

the bolted terminals damage the conductor, besides we could all get home/pub quicker.
 

Reply to cable burn out in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
444
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Being pedantic, the Crabtree 50A cooker switch is a 4500/1, which has 'cooker' printed on it. For a shower, you require the 4500, which is the...
Replies
3
Views
343
  • Question
Oh definitely, the amount of tails that I come across in consumer units barely nipped up is staggering, I always tighten them, wait a minute, give...
    • Like
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top