We are about to install a Hager VML114 (14way, 100A switch disconnector incomer) and intend to populate with RCBOs.
My understanding under 18th edition regs is that we need IP2X rating on the bottom of the Consumer Unit (prevent touch by fingers i.e. no gaps more than 1.25cm). We had been intending to fit glands to the bottom of the consumer unit.
Looking at the Hager CU, it appears that the bottom of the unit only has 4 rectangular knockouts on the bottom. What are the options here for an 18th edition compliant install?
I see that Hager are selling Closed Cable Entry accessories (VM03CB) or we could drill some new 20mm holes in the bottom. Any thoughts?
My understanding under 18th edition regs is that we need IP2X rating on the bottom of the Consumer Unit (prevent touch by fingers i.e. no gaps more than 1.25cm). We had been intending to fit glands to the bottom of the consumer unit.
Looking at the Hager CU, it appears that the bottom of the unit only has 4 rectangular knockouts on the bottom. What are the options here for an 18th edition compliant install?
I see that Hager are selling Closed Cable Entry accessories (VM03CB) or we could drill some new 20mm holes in the bottom. Any thoughts?