Cable Lugs Question | on ElectriciansForums
Discuss Cable Lugs Question in the Talk Electrician area at ElectriciansForums.net
Dammam, Saudi Arabia
The project specification says, "All compression connectors for 10mm2 (8 AWG) and larger conductors shall have a manufacturer's reference compression die number and conductor size printed or stamped on the connector".
Does Pin type lugs come with conductor size and die number stamped on the lugs?
Charzree if you are talking ferrels they make a special tool but you said # 8 and yes it should be listed the bigger ones even tell you how many times you have to crimp it and what size die you need. Really not to sure about # 8 but if no information is available on the lugs my advice is to pull on it as hard as you can which should be done on all connections. Smaller wire for controls especially because if not crimped tight they will pull out. I had a programmer going behind me on a job and he weighed about 300 pounds and couldn’t get my connections loose ?
On an other note has anybody tried crimping a flexible say 50 sq into a 50 lug ,they are never satisfactory and will easily pull out .
IS there a specific lug for flexibles
Generally speaking with flexible conductors often the lug is correct but the crimp dies are wrong, or crimper settings are wrong.
I've got adjustable manual crimper which have different settings for flexible or non-flexible cables.
It's a cembre TN120
Generally the ones I use are the SWA-brand hexagonal die sort and no option for changing size for fine/normal stranded cables. But recent attempts to pull out tri-rated as a sanity check showed it biting as well as I could tell.
I guess somewhere someone has studied the performance of the indent-style of crimp versus the hex-style, but never found it. I know that Cembre do both styles covering some common lug sizes, but again no real guidance as to which to choose!
I have an SWA brand set with the rotating hexagon dies that does 6mm up to 50mm too.
I've found that there are certain sizes of tri rate that just don't make a good connection when used with the right sixe hex dies, I can't remember if it was 25mm or 35mm but one of those two was really bad.
That's why the DNO don't allow tri rated in their meters. (whole current)
But the meters are clamp-style, not crimped lugs?
Certainly you need to use ferrules for flexible cables though.
Back to the hex-crimp tightness: I checked the 25mm SWA-brand tool & lug results and it is fine, no movement at any sane force I could apply by two-handed pull. But I have found that other brands of lug have a thinner tube and don't crimp properly in the SWA hex die. I guess the dent-style crimp tool might be more accommodating of tolerance but I have generally always liked the idea of the hex style of crimp as having more uniform pressure all round (if correctly implemented).
Klauke manufacture hydraulic crimps and connectors,and definitive spec,for both,for varied types of cable.
I can guarantee that when all three are matched...you are not pulling them apart :)
Reply to Cable Lugs Question in the Talk Electrician area at ElectriciansForums.net
The same socket can be used for different appliances, such as kettles... which will draw more than 5A The size of the cable determines how much...
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...