danieleither
For argument sake, lets say a cable is rated at 100A clipped direct, ambient temp 30 deg. Does this mean it can take a constant load of 100A in those conditions or is the rating based on cyclic current?
The reason I ask is on a recent install, following current cable guidelines we fitted a 35mm 4-core SWA XLPE cable to provide 150A per phase over a distance of 15 metres. At 150A constant load the cable has over-heated after 12 hours of operation (insulation melting).
I can't seem to find anything online about whether cable ratings are based on constant load or cyclic. Have we under-specced? If not, perhaps it's a damaged cable.
The reason I ask is on a recent install, following current cable guidelines we fitted a 35mm 4-core SWA XLPE cable to provide 150A per phase over a distance of 15 metres. At 150A constant load the cable has over-heated after 12 hours of operation (insulation melting).
I can't seem to find anything online about whether cable ratings are based on constant load or cyclic. Have we under-specced? If not, perhaps it's a damaged cable.