Have been asked to use 10mm swa to supply Granny flat with following spec from mcb on house csu.
Think should really be 16mmswa from separate switch in house. Am I missing something.
22 down lightslus 2 outside lights
10 2g sockets and 1 2g outside socket
electric oven
electric hob
electric shower
x 2 extractors
x 2 smoke detectors
3kw water heater
and x 3 poss 4 electric panel heaters
Quite a lot for 10mmswa. will first check with DNO to see if additional supply required and if not will supply separate feed from house via separate isolation switch.