Why not for a moment put the manufacturers spec aside other than they spec a 32 amp mcb
Depending on the installation method.the 4mm may be adequate,albeit at a push and not the more usual 6.0mm or 10.0mm
So in that respect the 4.0mm could be used
The manufacturer is specifying the cable size without all the other factors that help make that decision,how they have got this information would be interesting to know
I can understand specifying minimum 6.0mm or 10.0mm to try and leave room for lower current carrying capacity of a cable
It seems odd that a manufacturer is specifying a minimum cable size that is non standard
It seems as if they have taken the worst scenario installation method for the cable that will carry the diversified load of their appliance,then plucked a cable size out of the air
In the end, the cable capacity, installation method and the mcb rating is what will govern the need,but this manufacturers priority in the wiring regs should be considered by the IET in this day and age
Yes guys but the cable from the CU is not 10mm, I would say 6mm. So on the basis of the spec where does that put us. What about diversity.
Just in case, I'll take some 6mm to compare.Have doubts from a quick look in isolation.Normally is it not more usual to install 6mm than 4mm for cooker feeds. It was the 13A socket as the connection socket that caused my doubts. maybe it was oringinally installed for oven without hob and thus lower wattage. Why use a 13A socket - to make it easy for the then householder to plufg the oven in. Was it therefore wired to suit that householder without considering that someone may follow with a bigger oven. I cant find the spec for the oven at the moment but the ceramic hob had 2X 1700W : 2 X 1200W a 2K grill (I think) and a fan oven (dont know wattage of that one). Surely doesnt justify 10mm cable.
I'd ( recklessly ) ignore the oven manufacturers suggested cable size as they are clealy using a standard not used in the UK.
If you know the load of the appliance , whether in kw or amps , then a competant installer should be able to calculate the correct fuse / cable size.
And if the circuit is to be connected to a 32A mcb and isnt going to be covered with 2 ft of insulation , then i cant think of a single reason why you would need to use 10mm when 6mm will suffice.
The connection cable they specify is oddly : 5 X 1.5mm or 3 X 2.5 mm or equivalent.
This would seem to be 3 phase/ single phase cooker and the cable rating you are stating are those values for the cooker tail ?
Hi Fleetwood,
I have fitted a similar cooker oven to this before, ie. 3X 2.5 mm cable.
I seem to remember that you will struggle to fit 10mm cable, also if I recall the hob was split in two, ie. one 2.5mm to two plates, another 2.5mm to the other two (of four in total) and a 2.5mm to the grill and/or oven, bloody awkward, but doable.
Seeing as how the whole shooting match is wired in 6mm from the DB, you could do as I did and that is fit your 6mm to the centre blocks, and use 6mm or 2.5mm 'jumper links' to the the other two connection blocks, there are three connection points or terminal blocks on the one I did, there is no way you would be able to use 10mm cable to interconnect these.
Or you could just do as the manufacturer recommends and use 3X 2.5mm.
Ps. you will need to change that socket outlet to a cooker connection point.
As for diversity , well lets go through it together.....
10.5kw / 230v = 45A
diversity of cooker = First 10A + 30% of remainder + 5A for skt
10A + 11.6 A + 5 = 27A
Therefore 32A mcb on 6mm will be fine.
Also 32A mcb on 4mm will also be fine , installation methods and circuit length permitting.
If you mean Beko DVC663, the page on the manufacturer's website is here: Beko : Appliances : DVC663
You can download the installation instructions, which say to use 6mm² cable.
No reference to the odd cable spec from the OP. Maybe his cooker has a manual intended for another country?
The oven I'm dealing with is a BDVC 663 and the instruction book is different to the one you show. I wish this one showed using a 6mm tail lol. Cant seem to get a brochure download for the BDVC 663. I went to a shop for a look.
Hi Fleetwood,
Went in a shop for a peek at this BDVC663. Could only see one connection box on the rear though.
10.5kw / 230v = 45A
And wouldn't diversity apply to the tail - even though the manufacturer specifies a 7.5 equivalent.
Yes the one I did had only one connection box, but inside the cover where the cable/s terminate mine had three sets of connection blocks, it is awkward to get 3X 2.5mm to fit, which is why on the second one I just used a single 6mm and 'jumpers'.
On a slightly different model (this one specced 6mm), I noticed the blocks were interconnected internally with a metal comb.
What a pain! So if there are only three terminals in the block then I could get by by using one 6mm tail only but if there are three sets they have to be strapped out. Did you use 2.5 for the straps.