A new sub-main 3-phase supply to be installed on a large commercial site.....to supply a new food outlet (small building)
Sub main to be wired in SWA
Length of run 160 meters
Max load 65-70amps per phase (information supplied by catering company) no diversity has been applied by them.Also no allowance is required for any future expansion.

Not going to go into the full details.... but a disagreement exsits about the size of cable to use.
Would like to see what anyone on here would come up with..... :confused:
 
due to size power factor is requiered. However as none is givenn i have used the Impedancce rating (z) on the appendiz 4 chats.

assuming 90deg thermosessing SWa

I recon 75mm should do as that covers volt drop as well for sub mains distribution.

Watch opuit for your K factor if your using your SWA as an earth.
 
Last edited:
35mm and 70mm have been suggested....90 thermosetting
On impedance rating (z) does that incorperate a poor power factor if none is given?
what volt drop did you get on the 50mm?
5-core cable used....regarding earth
Thanks Scottsparky
 
Last edited:
changed the cable size sorry.

AS its a sub main cable i use 1% volt drop as it allows the other 4% so be used on the final circuits allowing smaller cables

remember your derating factors for burried cables.

if you lookm at appendix 4 then on the larger cables you will see three colums
r,x,z

r = Resistive
x = reactive
z = impedance

as you dont know what it is supplying use the cable impedance figure.
 
All the final circuits are within 10 mtrs of the DB....which shouldnt create too much of a problem with cable sizes on the distribution side.
As the sub main cable is the most expensive part and is practically the end of the circuit,the v drop allowance can be close to the max of 5%....surely?


Thanks for the replys




cable method has changed slightly
20% buired
80% clipped direct
 
Last edited:
be care full with that rememer Volt drop on lighting is only 3% appendix 12 table 12A page 358 in the regs.
As 20 is burried you have to use that derating figure.
 

Reply to Cable size-disagreement in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

  • Question
If your using 35mm or 50mm use 2 core SWA and use the armour as the earth, it'll cut down on price. I know people will comment on this but the...
Replies
10
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
945

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top