Hello gentlemen,
Please can someone guide me i would really appreciate. Customer has 2 x Car lifters fitted i assume its 16a each, single phase with a 13A, 3 pin plug. I wired 2.5mm ring main twin and earth clipped on the wall to 2 x double sockets. I ll also be using Rcbo as they been fitted outside.
First question is 2.5mm enough or I should have wired it on 4mm.
2nd question, what breaker size 32a or 40a and type plz B or C type.

Thanks in advance.
 
Hello gentlemen,
Please can someone guide me i would really appreciate. Customer has 2 x Car lifters fitted i assume its 16a each, single phase with a 13A plug.
How do you get 16A rating and a 13A plug?

What is the manufacturer's data saying?

I wired 2.5mm ring main twin and earth clipped on the wall. I ll also be using Rcbo as its been fitted outside.
First question is 2.5mm enough or I should have wired it on 4mm.
2nd question, what breaker size 32a or 40a and type plz B or C type.
The "standard option" for a RFC is 2.5mm and 32A MCB/RCBO. If they are intended for 13A plug use then that is fine.

If they actually need 16A outlets then you have to check the details of MCB curve, etc, based on the spec. They would be two separate breakers as 16A plug/sockets are not fused themselves and so need the supply breaker to provide overload protection.
 
How do you get 16A rating and a 13A plug?

What is the manufacturer's data saying?
Thanks for the quick reply mate at this time 12am lol. Sorry i think I have misguided you about the 16a. I have attached the picture of the lifter for your consideration.

The "standard option" for a RFC is 2.5mm and 32A MCB/RCBO. If they are intended for 13A plug use then that is fine.

If they actually need 16A outlets then you have to check the details of MCB curve, etc, based on the spec. They would be two separate breakers as 16A plug/sockets are not fused themselves and so need the supply breaker to provide overload protection.
 

Attachments

  • [ElectriciansForums.net] Cable size for car lifter ( ramps)
    IMG-20210626-WA0004.jpeg
    198.7 KB · Views: 69
How do you get 16A rating and a 13A plug?

What is the manufacturer's data saying?

I ll upload the manufacturer's data picture tomorrow from the 2nd ramp.


The "standard option" for a RFC is 2.5mm and 32A MCB/RCBO. If they are intended for 13A plug use then that is fine.

If they actually need 16A outlets then you have to check the details of MCB curve, etc, based on the spec. They would be two separate breakers as 16A plug/sockets are not fused themselves and so need the supply breaker to provide overload protection.
 
This a 3 phase lift according to the rating plate. It will need a 3 phase supply.
The customer has actually said to me that he has told the supplier to install single phase lifter as you can not see properly in the picture but its got 3 core SY coming out from the isolator. which the installer cut it for no f..k reason
 

Attachments

  • [ElectriciansForums.net] Cable size for car lifter ( ramps)
    IMG-20210626-WA0000.jpeg
    124.7 KB · Views: 82
I'd have gone 2.5/4mm radials to a rotary isolator for each lift, 2.2kw? (can't make out that picture fully) should be a dedicated circuit.

Lot more to this though, outside, circuit length, route????
 
I'd have gone 2.5/4mm radials to a rotary isolator for each lift, 2.2kw? (can't make out that picture fully) should be a dedicated circuit.

Lot more to this though, outside, circuit length, route????

Its actually going to the isolator built-in. Its just ring 2 x lifters clipped on the wall, about 20M long run
Yes 2.2kw each.
 

Attachments

  • [ElectriciansForums.net] Cable size for car lifter ( ramps)
    IMG_20210627_104532.jpg
    281.3 KB · Views: 47
  • [ElectriciansForums.net] Cable size for car lifter ( ramps)
    16247881086617792640485142363465.jpg
    286.2 KB · Views: 56
I'd be tempted to do two 4mm radials on 25 amp C type MCBs to 32 amp isolators. As the circuit is clipped this will give the future option of upgrading to 32 amp circuits if required. Isolator rather than Cdo Skt as this will negate the need for RCD if installation method permits.

As this is a workshop will the cable require mechanical protection?
 
Note the 2.2kW is the mechanical power output (P2) i.e 3hp. The electrical input apparent power will be higher due to both efficiency and power factor. Whenever possible, work from the stated line curremt which is shown on the plate as 20A; the starting current will be higher. 13A plugs would not be my choice of connection.
 
Last edited:

Reply to Cable size for car lifter ( ramps) in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
921
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

My wife’s Evoque gets about 32 miles on a full charge and I get about 28 miles on my F-Pace. I don’t know how long a full charge takes but I...
Replies
13
Views
1K
  • Question
To be honest James I use an app- Electrical Calculations. It auto calculates the cable size once you enter the specifics/parameters. Voltage...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top