Main supply cable entering my house is swa and measures 13.75mm outside diameter, don't know how many cores. I have electric wet central heating with a 9kw boiler plus immersion heaters, dishwasher, washing maching etc. all the normal stuff. House is all electric, no gas supply available here. Worry is the main cable looks small. Looking for some opinions from those more knowledgable than myself.
 
most likely be 16mm concentric cable. if DNO think that's good enough to fedd a 100A supply, then it;s good enough for me.
 
DNO will have supplied an appropriate service fuse to protect their cable.

You could always ring and enquire, although be prepared for a lot of faffing around.
 
Yes, cable is protected by standard 100 amp fuse. Became curious when main entry cable appeared to be smaller than 6mm2 swa I'm planning to use to supply a new garage. Concentric cable not something I've come across and may explain it. Thanks.
 
Straight Con = Combined N/E and only usable by DNO. Is that correct?

Not really, but 99% of the time, it would only be the DNO's using a concentric cable as a combined N-E cable!! They use split concentric as well, when replacing a damaged TN-S PILC cable, where the system hasn't been PME'd...
 
Not really, but 99% of the time, it would only be the DNO's using a concentric cable as a combined N-E cable!! They use split concentric as well, when replacing a damaged TN-S PILC cable, where the system hasn't been PME'd...

I see what you mean, when used by the DNO they use the outer conductors as a combined N/E cable but only they are allowed to do this.
We could of course use it in the same way as a 2 core cable, as long as the CPC function that it is lacking is provided for by other means.
Which is why I was wrong to say only the DNO can use it.

Cheers
 
I see what you mean, when used by the DNO they use the outer conductors as a combined N/E cable but only they are allowed to do this.
We could of course use it in the same way as a 2 core cable, as long as the CPC function that it is lacking is provided for by other means.
Which is why I was wrong to say only the DNO can use it.

Cheers

An example would be as a sub-main cable to an outbuilding on a TT system, where the earthing is being provided by roded systems. Only thing is, the cable, if taken underground would need to be ducted as they do not conform with BS7671 as a direct buried cable having no additional mechanical protection. The DNO's don't have to comply with BS7671, but even they only use it in the short lengths from the street distribution cable joint, to the their service heads!!

In reality, a straight concentric cable is rarely used outside of the DNO arena....
 

Reply to Cable size for main entry to house. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

  • Question
If your using 35mm or 50mm use 2 core SWA and use the armour as the earth, it'll cut down on price. I know people will comment on this but the...
Replies
10
Views
969
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top