Hi guys I have been asked to fit new shower and run new cable for it too, looking at regs book it would have to be reference method 103, which for 8.5kw shower would mean 16mm cable, can terminals in the shower take 16mm and the terminals in the isolator? I have tried looking for different cable routes but the board is downstairs and the bathroom is upstairs. 10mm is what is in at the moment. I don't usually do domestic electrical work so any advice would be great. I just thought 16mm was a bit overly for 8.5kw shower.
 
Hi guys I have been asked to fit new shower and run new cable for it too, looking at regs book it would have to be reference method 103, which for 8.5kw shower would mean 16mm cable, can terminals in the shower take 16mm and the terminals in the isolator?
Are you pulling sub main for it has well
what volt drop for this.
 
I just used one of those online volt drop calculator things and they come up with 16mm also. just I was looking at the regulations book for 10mm ccc and noticed with method 103 that it would be rated to 32 amps therefore I would have to go to 16 as the shower is 35.4 amps. I was just going to run 10mm but I guess I should go 16 to be in line with regs. I cant see any other different cable route. I have spoken to other electricians and they have said to just run 10mm but I would rather be safe than sorry. I usually work offshore so this domestic side is something im not really familiar with. thanks for your help
 
just used one of those online volt drop calculator things and they come up with 16mm also. just I was looking at the regulations book for 10mm ccc and noticed with method 103 that it would be rated to 32 amps therefore I would have to go to 16 as the shower is 35.4 amps. I was just going to run 10mm but I guess I should go 16 to be in line with regs. I cant see any other different cable route. I have spoken to other electricians and they have said to just run 10mm but I would rather be safe than sorry. I usually work offshore so this domestic side is something im not really familiar with. thanks for your help
Rule with a big thumb stick in 10mm
For a up grade of shower.
 
Hi guys I have been asked to fit new shower and run new cable for it too, looking at regs book it would have to be reference method 103, which for 8.5kw shower would mean 16mm cable, can terminals in the shower take 16mm and the terminals in the isolator? I have tried looking for different cable routes but the board is downstairs and the bathroom is upstairs. 10mm is what is in at the moment. I don't usually do domestic electrical work so any advice would be great. I just thought 16mm was a bit overly for 8.5kw shower.
You don't mention in your post the length of the run of this circuit.
 
Hi guys I have been asked to fit new shower and run new cable for it too, looking at regs book it would have to be reference method 103, which for 8.5kw shower would mean 16mm cable, can terminals in the shower take 16mm and the terminals in the isolator? I have tried looking for different cable routes but the board is downstairs and the bathroom is upstairs. 10mm is what is in at the moment. I don't usually do domestic electrical work so any advice would be great. I just thought 16mm was a bit overly for 8.5kw shower.
Well there is a little bit of history in the making here for me. An 8.5 kW shower wired in 16mm?.Am really curious to know the installation conditions for this one. I must assume it is immersed in insulation and on the top floor of a 3 story structure?
 
16mm for the run through insulation then 10mm from an isolator switch of you need to drop cable size.
 

Reply to cable size for shower in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Being pedantic, the Crabtree 50A cooker switch is a 4500/1, which has 'cooker' printed on it. For a shower, you require the 4500, which is the...
Replies
3
Views
338
  • Question
Better off with the click prw213 as it has twin screw termination.
Replies
9
Views
986

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top