cable size help needed please | Page 3 | on ElectriciansForums
Discuss cable size help needed please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
hi everyone. thanks again for all the advice. after viewing the job this morning. it is a 200m run on a TT system. the stable s actually only having lighting and sockets. there is only going to be 3 doubles so a 16a radial will do for that. and for the lighting there are going to be 8 led floods at 8w each giving 64w in total
64w would give .28amps right?
plus the 16amp for the radial
giving me a design current of 16.28amps
is this correct?
im thinking a 25mm 2 core armoured from the house to the stables and then 25mm earth on a earth rod at the stables
could any of you tell me if im right, or close. or have i got everything wrong. i think i worked the volt drop out at 7.7a
by using a little diversity, reduce your design current to give a VD of 3%, this will comply for the lighting.
edit: just done a quick calc. and i get a current capacity of 19.5A to give a VD of 6.9V.
Thanks for your reply telectrix, can you please tell me how you got 19.5. And 6.9. I also forgot to mention there will be a supply for a alarm as well, prob another 3 or 5 amp. Do you think 25mm swa would be enough, or would 35mm be better?
Reply to cable size help needed please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I'd always go for 25mm2 5core over 50mm2 3core, with the cores paired up. Considerably cheaper, easier to terminate and ready to go, if ever 3...