I have a customer whose electric shower has stopped working. It has previously been working fine for a couple of years. No problems before hand, no faults on the board or tripping out.
upon inspection it looks like the supply cable is undersized. He’s asked me if this would have caused the shower fault? as I understand an undersized cable would more likely effect the circuit or MCB an not the appliance itself.
 
Volt drop can effect the shower if the cable is undersized, resulting in the shower not working correctly but you have stated that it worked fine for a couple of years.
 
Undersize cable is most unlikely to be a factor unless it is so drastically undersize that it has melted, or it has burnt out at the terminations. The only likely impact on the shower itself would be a slight reduction in maximum water temperature if the cable is also long and the voltage drop significant.
 
Customer is trying to c
What makes you think the cable is undersized?
The customer is trying to establish whether the plumber who installed it is at fault for the shower breaking. Plumber says it was like for like. No faults reported during usage. Shower broke after 2 years and now there’s an issue with the cable size. I wasn’t sure whether a smaller cable size would break the shower. My thoughts were it would only effect the cable or trip the fuse
 
I've no idea why you would expect undersize cable to trip the MCB! Showers of this power will operate on 2.5mm² T+E and we've seen it done, but the cable gets very hot and floppy. Subject to voltage drop, 2H4 4mm² MICC on the surface is fully rated for the purpose and would be a perfectly good choice. 2H2.5 is just barely undersize but would function perfectly well.
 
Last edited:
Agr
I've no idea why you would expect undersize cable to trip the MCB! Showers of this power will operate on 2.5mm² T+E and we've seen it done, but the cable gets very hot and floppy. Subject to voltage drop, 2H4 4mm² MICC on the surface is fully rated for the purpose and would be a perfectly good choice. 2H2.5 is just barely undersize but would function perfectly well.
Agreed. But would it effectively break the shower? I can’t see how?
 
No. Excess voltage drop would affect the shower by reducing the maximum heat output, but not damage it. If the shower has electronic controls, then at some critical level of drop, they would stop working and the shower would switch off, or cycle on and off. I would expect it to work at 190V (230V -10% - a bit of leeway) which would typically mean 40V of drop. So when the mains volts are normal, even 150 metres of 6mm² would not stop it working.
 

Reply to Cable size to electric shower in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
433
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There are two reasons for a fuse/mcb they are: 1) fault conditions - which must exist always, and be capable of operating for all points on the...
Replies
4
Views
936
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top