I'm struggling to work out cable size.
a lighting circuit in a office with the distribution board next door,having three cables chased up.to the suspended office room next door then run in basket tray for two meters before separating to each circuit.
In=6
Ca.30 degrees seems a high ambient temperature
I'd of thought room temp is more like 20 so I don't get that
I put 25degrees so x1.03
Cg three circuits bunched in air or embedded or enclosed
So I put x0.7
Then the protective devise won't be a bs3036 fuse
So x1
6/1.03x0.7x1 =8.32 now I don't get how to use table f5 to get cable size
I then tried with cooker
9kw
/230 =39a
Diversity =18.73 a which sounds low for a cooker
In =20
Ca1 cg1 cf1
So again I have 20 as current carrying capacity but how do I get the cable size from the table
And am I right so far thanks