Hi everyone,

Ive been asked by the customer to supply a 16mx8m metal shed, it will be used as for his hobby of working at old cars it will have 5 circuits,
supply to another out building 50m away with a couple of sockets and 5 lights, prob 20amp be enough
a ring main
lighting circuit 6-8 led lights
roller door
car lift with 3hp motor.
The problem is the shed is 115m away from the house, hes asked me to price for a 63amp and 40amp supply. From my cable calcs a 2-core 16mm swa will have 12.88 volt drop for the 40 amp supply and 20v for the 63amp supply(too much). The calcs for the 25mm swa is 12.68v at 63 amps.
Ive worked out using k1/k2 X S that the armour is ok for the cpc. I will be fitting a 100ma S-type at the house end and driving a spike in at the shed end.
Is there any other factors i need to take into consideration for that run of cable?
Also only looking to use two cores to keep the cost down. Do for a pound what any fool can do for a fiver :)
Thanks in advance.
 
I must admit this sentence has perplexed me, and I'm probably missing something.
If we were talking about the main earthing conductor for the installation at the house I'd get it.
But we are talking about a circuits CPC here aren't we, so doesn't it just have to meet 543.1.3, and be equal to line conductor if less than 16mm sq?
think he means as a bonding conductor. see post #15.
 
If the supply is TN-C-S and you don't TT the remote building then you need 10mm copper equivalent for the CPC.

For 2-core SWA that only happens by time you get to 70mm, expensive!

If smaller SWA (but above 10mm) it can be cheaper to run a 10mm coper CPC in parallel with the SWA.
Its a TT system at the house and will be made TT at the shed, Im not using the armour as a cpc for the shed, only for the sub-main cable which will be protected by a 100ma s-type RCD. I will install a spike at the shed.
 
Its a TT system at the house and will be made TT at the shed, Im not using the armour as a cpc for the shed, only for the sub-main cable which will be protected by a 100ma s-type RCD. I will install a spike at the shed.
Is there any chance the house will become PME (TN-C-S) at any time? If not, then I would use the armour to link both as well as an earth rod. Generally the lower the Ra the better and multiple earths allow less chance of a single point of failure.

Will the sub-main be off the supply (i.e. split tails and the 100mA delay-RCD as an isolator) or is it coming off the house CU that already has a 100mA delay RCD up-front? Fine in both cases, but ideally all final circuits at the out building on 30mA RCD/RCBO so you don't lose the lot on a fault.

If it is planned as a workshop you might also want to consider some LED lighting with built-in emergency battery, that way you don't end up plunged in to darkness with tools spinning, etc, if the light supply goes off for any reason (including supply interruption).
 

Reply to Cable size in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
707
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
If your using 35mm or 50mm use 2 core SWA and use the armour as the earth, it'll cut down on price. I know people will comment on this but the...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top