Hi all - can someone confirm my thoughts please

Here is the situation:

  • 6 floor hotel
  • 45 bedrooms over 4 floors
  • bottom 2 floors are reception and kitchen - not worried about these at present
  • 3 phase supply coming into building - 1 phase per 2 floors - current setup
  • Each floor has 2 DBs
  • The manager now wants to put separate DBs in each room (I am pushing for RCBOs in main floor DB and no DB in each room)
  • 12 rooms per floor (on average) (6 rooms per DB)
  • The supply cables from main supply DB to floor DBs are traveling up an old shaft over 100mm from surface - no need for RCD protection
  • Between floor DB and Room is less than 50mm from surface - would need 30mA RCD protection via RCBOs

The manager wants separate DBs in each room so if a room develops a fault it wont effect anything else - RCBOs in main floor DB would do this anyway - separate circuit per room - (1 for lighting and 1 for sockets) - also thinking about discrimination here! - with 30mA RCD in each room.

I need to work out:
  • cable size to the main floor DB (from the basement 3-phase supply)
  • cable size to the individual room DBs

Each room has:
  • 1 kettle
  • 2 bedside lamps
  • main lamp on ceiling
  • 4 sockets in total
  • shower is NOT electric

If im not mistaken each room would draw 25A max first thing when someone boils the kettle and using their hair dryer/straightener
Was thinking about a 4mm radial to the 4 sockets and 1.5mm to lighting

Was thinking a 10mm cable from main floor DB to individual room DB (could get away with 6mm as max current would be less than 36A - RCBO in main floor DB would be a 40A)


Not sure about the cable from floor DB to main supply DB - it currently has 16mm T&E installed - not sure if this is enough or would have to be 25mm?????? - thought please
 
Most the hotels i've tested usually have 1 DB supplying 2 rooms, located in the riser between the 2 rooms. Usually fed by a 10 or 16mm T+E, protected by a 32 or 40A MCB back at the sub board on the same floor. Never seen a sub board supplied by a 16mm T+E. They're usually a 25mm SWA at least. Good luck!
 

Reply to Cable Size in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

  • Question
There is also the ongoing problems if this is a gendered changing room.... For example, 2 or 3 burly male soldiers (you said it was an officers...
Replies
5
Views
868
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
942

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top