hi all again its another cable size Q

lighting is ran in conduit and supply 8x ft batton fittings 50w each
grouped with 3 other circuits ran in single cores
total lengh is 100m
230v


can any one give me advice on the size of cable needed, i know the usual is 1.5 for lighting but it states this is industrial.

what is the common lighting cable size in industrial places eg light wareouse
 
In the warehouse where I work the calc is worked out and the cable size is selected as per the calc.
We do not want to put in to small a cable but on the other had we do not want to put in oversized cable which will cost more.


You can use 1.5mm for the loads above - volt drop will be approx 5v.
Circuit will pull approx 1amp whilst running (maybe more on start up depending on lighting type)

I do remember that when calculating for lighting in a domestic dwelling that all fitting must be calculated as 100w but i'm not sure for commercial.

I have calculated the above using 8 x 50w as the load.

You will need to have the job checked as certain factors will change the calculation, we have run lighting in our factory on 2.5 and 4mm in the past.
 
Last edited by a moderator:
HI JIGA!

"can any one give me advice on the size of cable needed, i know the usual is 1.5 for lighting but it states this is industrial."

Irrespective of whether it's an industrial installation you will need to consider all aspects of design. You have listed some of the factors that are needed to be considered when designing a circuit. However, nothing should be overlooked and you should revise this fully. For example the type of cable, ambient temp etc....

It's not uncommon to find 2.5mm for lighting in industrial installations.

Hwyl!
 

Reply to cable sizes for lighting in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that...
2
Replies
29
Views
2K
  • Question
Hi Kevin, Thanks for the reply. No I didn't test them individually, as when it tripped a couple of times, I changed the rcbo out for an mcb and...
Replies
5
Views
1K
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
Replies
21
Views
990
nicebutdim
N
  • Question
wouldn't surprise me if we adopt this sooner or later...
Replies
7
Views
1K
  • Question
Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks