Was carrying out a PIR today.
10 x low bay lights supplied via 20A MCB
Cable to klix units is 2.5 which is fine but from klix to lights is 1.5

should this be reported (20A MCB too large for 1.5mm)
 
i=p/u your thoughts are fine in theory but if there is say a fault with the fitting and it was drawing 19A for instance then the 1.5mm flex would not be able to handle this and the MCB would not trip
 
mopst of the clicks i have ever fitted, have been fitted to lights that have incorporated a fuse. if the light started pulling too much current, then the 1.5mm cable is protected by that fuse. this is called backfusing. if the cables is damaged, then the device further up the line will protect the cable from short circuit, Zs permitting.
 
This is no different from using 0.75mm² for pendants, or spuring off from a RFC in 2.5mm².
The cable upt to the Klix has to be sized to carry the current of the whole circuit, whereas the cable from each Klix only has to carry the current for that particular fitting.
 

Reply to Cable sizes for lights in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
603
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
239
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top