Hi Guys
I have been arguing with a guy at work about some supplies he's been installing.
He has installed two 16 amp three phase sockets using 4mm swa clipped and in trenches of about 30 meters he's protected it with a 32 mcb.
The swa terminates in a switched fused isolator with 32 A fuses in. Out of the fused terminals he's used 2.5 singles to the sockets which are about 500mm away.
I said the singles should be 4mm or the fuses should be 16 A.
to protect the 2.5 s and 16 A sockets.
He was originally going to use 2.5 swa with a 32 A mcb to supply this installation his argument was the machines wont pull more than 5 amps each. Any comments please just needed to vent my spleen thanks
 
Well if his maximum demand is only 5 amps perphase why did he select a 32 amp MCB when he could use 10 amp depending on the inrush current you are correct in saying that the fuses should be 16 / 20 amp but as ive said could easily be 10 amp .(10 amp due to the max demand being so close to the MCB / Fuse rating dont want it to get hot )
 
A 16A rated socket outlet protected by a 32A fuse doesn't sit quite right with me. Even though the downstream load is as you say rated at 5A so can draw no more, it isn't a fixed load and something else could be plugged in at any time by anyone which may cause a problem!
 
A 16A rated socket outlet protected by a 32A fuse doesn't sit quite right with me. Even though the downstream load is as you say rated at 5A so can draw no more, it isn't a fixed load and something else could be plugged in at any time by anyone which may cause a problem!

i missed that one very sore eyes to night after doing a BBq for a load of brownies ,yes i know its october and the bbq should be in the shed but were in wales and it always feels like summer
 
16a sockets should be fused correctly i would say - it may not cause a problem here with dedicated loads


if they were SP sockets -appliances could easily be added on later to leads etc. resulting in overcurrents and 'disconnection times' not being met with a 32amp
 
Got to be careful here as 3 or 4 core 2.5mm XLPE SWA (90degreesC) has a tabulated CCC (It) of 32A+ in some cases but that is pushing it to say the least IMO.

PVC SWA on the other hand doesn't. I think we all agree that 2.5 should not be protected by a 32A MCB as in most cases with factors applied the formula Iz>In>Ib is not adhered to.

It's 20A or possibly 25A max for me.

Is this particular machine on a plug and socket arrangement also???
 
Ill be honest and agree with lenny i would never use any higher than 20 amp mcb on a 2.5mm .twe swa or other reason being its what happens after its installed , as i have said in a post in our area they have installed 200 of insulation over the cables whic changes the installation methods to 103 which means the cables current carrying capacity reduces dramatically so if you designe for worst case values ratings you cant go wrong ,having seen a family wiped out in a house fire i feel its the best way to work
 
I agree I always go on the side of caution and step up sizes just in case. Especially in industry , Insulation wont be a problem but you never know what will be added to the machine in the future.
 

Reply to Cable sizing in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

The total current capacity of the system in amperes is the same as the per-phase rating when referring to a balanced three-phase system. Thus, a...
Replies
4
Views
469
  • Question
Do you know what percentage of scheme registered electricians are registered to sign off 3rd party work? Even better would be a poll of how many...
2
Replies
25
Views
2K
nicebutdim
N
  • Question
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that...
2
Replies
29
Views
2K
  • Question
If your using 35mm or 50mm use 2 core SWA and use the armour as the earth, it'll cut down on price. I know people will comment on this but the...
Replies
10
Views
921

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks