Hi Guys
I have been arguing with a guy at work about some supplies he's been installing.
He has installed two 16 amp three phase sockets using 4mm swa clipped and in trenches of about 30 meters he's protected it with a 32 mcb.
The swa terminates in a switched fused isolator with 32 A fuses in. Out of the fused terminals he's used 2.5 singles to the sockets which are about 500mm away.
I said the singles should be 4mm or the fuses should be 16 A.
to protect the 2.5 s and 16 A sockets.
He was originally going to use 2.5 swa with a 32 A mcb to supply this installation his argument was the machines wont pull more than 5 amps each. Any comments please just needed to vent my spleen thanks