If there are any mettalic pipes or other extraneous conductive parts [metal structures in contact with the ground],then the minimum size cable will have to be 10mm2 ,unless you TT the installation in the outbuilding.



spark1
 
If there are any mettalic pipes or other extraneous conductive parts [metal structures in contact with the ground],then the minimum size cable will have to be 10mm2 ,unless you TT the installation in the outbuilding.



spark1
Why would you do that.The Op stated that the building is only a metre away from the house.Personally it doesn't need spiked and i would use the existing cable for the power and lighting by adding a spur for the lights:cool:
 
Granted there is a 2.5mm there at the moment, but is it protected? open to the elements? if its a job and he wants to get repeat business he should do it in Swa. I accept it might be more costly but wait till the homeowner gives him hassle when the cable fails due to being exposed to the elements
 
Granted there is a 2.5mm there at the moment, but is it protected? open to the elements? if its a job and he wants to get repeat business he should do it in Swa. I accept it might be more costly but wait till the homeowner gives him hassle when the cable fails due to being exposed to the elements
If it's only feeding 1 socket,i'd pull the cable back to the point of exit from the house and put it in pvc conduit.:D
 
Macca . the outbuilding is remote from the existing main building.....be it 1m. or 100m. therfore if it is to utilize the existing fault protection of EEBAD [ADS],then the equipotential zone extends to the outbuilding which means 10mm2 bonds to any extraneous conductive parts whithin it. Alternatively the outbuilding can form its own equipotential zone by creating aTT system.............if no extraneous conductive parts then no problem !


spark1
 
Macca . the outbuilding is remote from the existing main building.....be it 1m. or 100m. therfore if it is to utilize the existing fault protection of EEBAD [ADS],then the equipotential zone extends to the outbuilding which means 10mm2 bonds to any extraneous conductive parts whithin it. Alternatively the outbuilding can form its own equipotential zone by creating aTT system.............if no extraneous conductive parts then no problem !


spark1
So what you're saying is,if you had a shed in your back garden with an existing supply already feeding a socket,you would still spike the shed.:confused:
 
If there where extraneous conductive parts insidethe shed and the supply cable was less than 10mm ,on a tncs supply,then i would probably run in a 10mm2 seperate bonding conductor from the M.E.T in the house....if this was not easily done then yes i would TT the shed........if no extraneous conductive parts then the problem does not exist.....The o.p doesnt say either way on this issue
 
If there where extraneous conductive parts insidethe shed and the supply cable was less than 10mm ,on a tncs supply,then i would probably run in a 10mm2 seperate bonding conductor from the M.E.T in the house....if this was not easily done then yes i would TT the shed........if no extraneous conductive parts then the problem does not exist.....The o.p doesnt say either way on this issue
Ok mate i give up.You win.Goodnight.Just about to watch Rollerball on Ch5
 
It wasnt a competition Macca..just trying to help the o.p.

..your team qualified for next seasons Champions league eh ! Congrats....Liverpool fan myself....will see you there

Goodnight !



spark1
 

Reply to Cable to outbuilding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
499
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
973
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

Yeah, been unwell but better late than never!
2
Replies
24
Views
2K
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
454

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top