I am running a load of cable tray at the minute. I said it required cross bonding with 4mm cable, but my boss said it wasn't required as we are using metal joiners...........
Who is right?
Who is right?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Cable Tray cross bonding? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
'Cross bonding' ????........you may need to link joints in the tray with a copper link to ensure earth continuity if the joints are not electrically continuous ,but 'cross bonding' ?..is this the same as the ancient-mythical practice of wasting ones time linking boiler pipes together etc.?
i have put miles of tray in on jobs, only ever used tray joints for continuity, bond final ends of tray onto DB,s or panels with 4/6mm earth bond with lugs. no need to cross bond to other services.
Cable tray (or other steel containment) containing only sheathed cables, even if bare MICC, is not an exposed conductive part of an electrical installation. Therefore it is not required to be connected to the MET by a cpc.
If it is earthed this would be down to the job spec or working practices.
However, if likely to introduce earth potential from one building or installation to another, main equipotential bonding would be required at point of entry.
This is a specific topic covered in IEE Guidance Note 8 : Earthing and Bonding.
Well definitely gonna earth it because , although not an exposed conductive part, I certainly consider it an extraneous conductive part.
I know it doesn't fall under the bonding requirements of 411.3.1.2, but this and the ceiling grid will be earthed, in the event that they may become live under fault conditions.
Not got guidance notes 8 (got 1 and 3), so can't look it up
Unless the cable tray comes out of the ground how could you define it as an Extraneous conductive part if it cant introduce an earth potential. Of course if the cable tray can introduce an earth potential then it would need to be bonded accordingly. there is also no requirement to earth a ceiling grid, since ceiling grids are push fit you would have to link every length of grid together to ensure contiuity, just as you suggest doing with the cable tray.
Sometimes bonding everything metal you can get your hands on can lead to an increased risk of a shock.
just another bit to the Argument who is going to pay for this cross bonding If your boss has said NOT to do it and you go and do it will he pay both your time and material for doing it??
why would you consider bonding every link? thats going to take you for ever and for what? youll gain continuity by your roofers/links or what ever means of connection you make between the tray.
each to their own but a supplementary bond at the start would suffice.