The consensus here seems to be that cable tray cant be used as a protective conductor
Whilst I agree with most of the points against thats been posted
I would like to refer you to 543.2 Types of protective conductor
Now whilst I have never considered the question before because like some have pointed out, the lack of need for this and the problems that are associated with it make it a no go either way
If you read 543.2.2 vi
A protective conductor may consist of one of the following
Quote
A metal conduit etc etc etc or electrically continuous support system
Now I think a tray can be defined in this way and therefore as long as it is continuous there it seems to fit the bill as a protective conductor but probably not as a circuit protective conductor
As an aside to this comment My understanding was that in the 16th edition bonding of a tray was not necessary unless it exited/entered a building
Does the 17th advise on this
Whilst I agree with most of the points against thats been posted
I would like to refer you to 543.2 Types of protective conductor
Now whilst I have never considered the question before because like some have pointed out, the lack of need for this and the problems that are associated with it make it a no go either way
If you read 543.2.2 vi
A protective conductor may consist of one of the following
Quote
A metal conduit etc etc etc or electrically continuous support system
Now I think a tray can be defined in this way and therefore as long as it is continuous there it seems to fit the bill as a protective conductor but probably not as a circuit protective conductor
As an aside to this comment My understanding was that in the 16th edition bonding of a tray was not necessary unless it exited/entered a building
Does the 17th advise on this