I'm looking at an install of a double oven cooker ... 11.3kW maximum demand ... and rather than use 10mm T&E for the final connection I have been looking at the CCC tables in Appendix 4
Table 4E2A on page 368 (3rd Amend of 17th) states I should be able to use a cable with 6mm CSA conductors, but can anyone tell me what the name of the cable is as referred to in Table 4E2A.
The highest CCC that I have been able to get confirmed is for 6mm "TQ" which is to BS6500 and can handle up to 48A ... frustratingly close to the 50A circuit I need to install.
Doe anyone know what British Standard number cable that Table 4E2A is referring to???
Looks like I will have to fight with some 10mm T&E, but it would be nice to make the final connection in 6mm flex.
Any help would be greatly appreciated.
Regards,
Paul