Did a consumer unit change the other day only to find that all the down stairs sockets had been buried in concrete. It must have been a wooden floor then the good old builder just poured concrete in!
Insulation readings are L - L = 4.2 M ohms, L - E = 2.21 so just ok. Zs is ok.
The problem is the cert. In comments i have put about the concrete and insulation readings could change at any time. Recomended a rewire of sockets.
Under reference method i put * then in "remarks" *no reference method because of being laid in concrete.
Next inspection i put 12 months.
Do you think this is ok or is there anything else i should do?