Just wondering if someone could help me out with this one

Basically I'd like to know what's the maximum load (single phase) a 4 core 6mm SWA could deliver if cores were connected in parallel

SWA in buried under ground and the length is three hundred meters

The cable used to supply a 3 phase pump on a farm many years ago. The farmer would like to renovate pump house, and yep you guess it, want power down there.

Used a cat scanner to find and determine length.

Any help would on this would be much appreciated

Best regards

Dave
 
You need to ensure the safety of the two cables, in general the regs advise adding the CCC of each core.
In practise the CCC may be slightly greater but this is not accounted for in the wiring regulations.
Have a look at 433.4 and 434.4.
 
Were you thinking of just using the armour as the earth? Or is it TT at the far end?
Don't know what your calcs say but the steel isn't as good as copper, especially over 300metres.
 
Your average caravan hook up is 16A, but you could make a practical view on max demand being a lot less than 4x16A.
Could limit the hookup supply to 10A, maybe?
 
I have told him my concerns, when its cold the heaters go on and the kettle goes on and so on...
I'll tell him the pump house is the limit.

He'll tell you white is black, when you tell him it's white he doesn't really give a .........
 
Shoot me down if I am barking up the wrong tree, I get conductors in parallel but what columns in Table 4D4A or 4E4A are you using to determine the current carrying capacity of the cable. Column 6 refers to a single phase load in a 2 core cable, however you have a single phase load in a 4 core cable so does this equate to Column 7 which is a 3 or 4 core cable on a three phase load. My view is Column 7 due to the quantity of conductor and not the fact it is single or three phase.
 
Your CCC would be 92A and your pump house perhaps a maximum of 50A so that would leave you 40A to divide among the caravans.
However your volt drop will be well beyond limits at that loading, especially as you want to extend further for the caravans.
I have just checked and I think you would need to keep your current below about 6A to keep within 6.9V (3%) drop over 300m with a 12mm² cable!.:):rowboat:
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Cables In Parallel, Max Load?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
29
Unsolved
--

Advert

Thread statistics

Created
bogney,
Last reply from
Knobhead,
Replies
29
Views
4,795

Advert

Back
Top