hello all
Im a trainee and have a question about Ib,
If im working out cable calculations for a 63amp sub main with a 6amp and a 32amp mcb then what would my Ib be? is there a way or do you need to know wattage such as a 3kw water heater for example? please help
thanks
Terry
 
if it's a 63A sub-main, then i would take my Ib for the cable supplying it as 63A. the existing 32A &6A circuits could be increased in the future.
 
No !!
do not skip Ib
do not pass go
do not collect ÂŁ200
;-)
in the most simplistic terms your max Ib will be the 32a mcb + 6a mcb = 38 A
then you can apply diversity to reduce this figure if you know what loads are to be connected.
never ignore this basic assessment , its the starting point for all cable calcs.
 
first, Iz>In>Ib. i.e. if your design current (Ib) < fuse rating (In) < CCC of cable (Iz), so if you IB is 63A, then In >63 (e.g. 80A) so Iz needs to be >80A (e.g. 90A)
 
No !!
do not skip Ib
do not pass go
do not collect ÂŁ200
;-)
in the most simplistic terms your max Ib will be the 32a mcb + 6a mcb = 38 A
then you can apply diversity to reduce this figure if you know what loads are to be connected.
never ignore this basic assessment , its the starting point for all cable calcs.


i would allow for increased loading on the sub-main, unless it's specifically designed for a set purpose, in which case i agree with you.
 
It all depends what you are designing the actual sub-main circuit for? But whatever you as the designer choose it has to meet the basic concept of Ib < In < Iz.

If you want a sub-main to take 63A then design it for Ib = 63A -- as Tel states.
If you want a sub-main to take 6A and 32A then design it for Ib = 38A -- as Biff states.
 
Hi TerryCarl
I agree with Telectrix. It's not a question of what might happen later, it's a question of what fuse is protecting the cable in question from overheating?
63A ?
Ib < In < Iz is the first commandment.

Laurie
 
thank you guys
so the main switch on the sub would be greater than the fuses combined in the sub and the fuse on the main board would be greater than the main on the sub!.... also, if burying the SWA how would i know the Ca factor, do i take it as 1 then add Cs and Cd, something Ive never been shown so not too sure what K.m/W means or how to apply it
Thanks
 
thank you guys
also, if burying the SWA how would i know the Ca factor, do i take it as 1 then add Cs and Cd, something Ive never been shown so not too sure what K.m/W means or how to apply it
Thanks
Ca would generally be 1 because the the sub ground temperature is fairly stable and unless you have specific circumstances 20oC is fine.
kelvin meter per watt is is stating the temperature change over 1m for each watt of energy. Again if you have a standard soil type you can generally assume your soil is suitable since the regs give average values to make calculation easier.
When adjusting your In you divide In by the product of the factors you are applying to get the value you need to find in the appropriate table.
 
thank you guys
so the main switch on the sub would be greater than the fuses combined in the sub and the fuse on the main board would be greater than the main on the sub!.... also, if burying the SWA how would i know the Ca factor, do i take it as 1 then add Cs and Cd, something Ive never been shown so not too sure what K.m/W means or how to apply it
Thanks

Your protection device for sub main circuit in the main board does not need to be greater than the main switch in the sub main board, because the Main switch is just that SWITCH there is no fuse in it. The 63A label on your switch just saying that this switch can safely operate up to 63A, that’s all. Think about, it is like installing the 2 way garage consumer unit with main 63A RCD incomer and your 2 MCB’s, 32A and 6A, you surely not going to come from 80A MCB in the house are you? Imagine the size of the cable to garage, insane.
In your case I would normally go by MCB sizes adding up and applying diversity or the rule of thumb 0.4 factor to it if it is only 2 way board, But if it is more spare ways I would not apply the diversity and in that way it would leave me with provision in the future.
 

Reply to calble calculation Ib in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
325
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
852
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
973

Similar threads

  • Question
Hi tssxrr, I am also doing my assignment on the same topics. would you mind sharing the documents which you have done so I will have rough idea...
Replies
1
Views
2K
I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
503

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top