Hi, searched but still niggling problem need help on...
Installation: -
4mm earth to earthing electrode (rod) Ra 42ohm
Zdb 33ohm
1361 60A main fuse
16mm tails
cant get acceptable result for using adiabatic as disconnection time too high (higher than 5 secs with that Zs reading)
no frontline RCD protecting tails.
What would the minimum bonding size be? (2mm therefore 4mm wiring?)