JuniorSparky
Hi everyone,
On the drawing it says the system's TN-C-S with declared Z[SUB]e[/SUB] = 0,008 Ω and prospective fault current declared as 50kA
When I calculate I[SUB]f[/SUB] = U[SUB]o[/SUB] / Zs = 230 / 0,716 = 321 A . With this value there's no way to match with 10A curve at fig. 3A6 (appendix 3)
But if I calculate the disconnection time with t = (k[SUP]2[/SUP] x S[SUP]2[/SUP]) / I[SUB]f[/SUB] = (115[SUP]2 [/SUP]x 1[SUP]2[/SUP]) / 321[SUP]2[/SUP] = 0,13s (k=115)
If I actually have to calculate cpc csa, I can't find a way to do that because I can't match the 10A curve for circuit breaker and get a value for t !?
What's the role of the declared prospective fault current - 50kA?
Do I have to use that formula to calculate disconnection time or use figures from appendix 3?
PS: Here is the beginning of my calculations!
I'm doing C&G 2357 and hopefully one day I'll become good electrician like you all.
I'm currently doing my 304 home assignment and I'm a bit confused.
I have to find min csa of live conductors for current-carrying capacity and voltage drop for 5kW, 400V three-phase machine. Ambient temperature - 20[SUP]o[/SUP]C.
- So I find I[SUB]b[/SUB] = P / (√3 x V) = 5000 / (√3 x 400) = 7,2 A
- then choose for I[SUB]n[/SUB] = 10 A ; choose 10A BS EN 60898 - type D ; Reference method B
- Correction factors: C[SUB]a[/SUB] = 1,03 ; C[SUB]g[/SUB] = 0,65*
- I[SUB]t[/SUB] => I[SUB]n[/SUB] / (C[SUB]a[/SUB] x C[SUB]g[/SUB]) => 14,93 A
- choose cable with csa 1,5mm[SUP]2[/SUP] and I[SUB]t[/SUB] = 18,5 A
- check voltage drop - Vc = (mV x I[SUB]b[/SUB] x L)/1000 = (29 x 7,2 x 23)/1000 = 4,8 V (L = 23m)
- check for shock risk - Z[SUB]s[/SUB] = Z[SUB]e[/SUB] x R[SUB]1[/SUB] x R[SUB]2[/SUB] ; R[SUB]1[/SUB] x R[SUB]2[/SUB] = 30,20 x 23 x 1,02 = 0,708 (1,5mm[SUP]2[/SUP]/1mm[SUP]2[/SUP] cpc)
* I'm confused for the grouping factor as well. There's a note under table 4C1 saying the table can be used only for equal loads. In my task there are 4 different loads! Can I still use that table to give a vale to my grouping factor
Thank you in advance
On the drawing it says the system's TN-C-S with declared Z[SUB]e[/SUB] = 0,008 Ω and prospective fault current declared as 50kA
When I calculate I[SUB]f[/SUB] = U[SUB]o[/SUB] / Zs = 230 / 0,716 = 321 A . With this value there's no way to match with 10A curve at fig. 3A6 (appendix 3)
But if I calculate the disconnection time with t = (k[SUP]2[/SUP] x S[SUP]2[/SUP]) / I[SUB]f[/SUB] = (115[SUP]2 [/SUP]x 1[SUP]2[/SUP]) / 321[SUP]2[/SUP] = 0,13s (k=115)
If I actually have to calculate cpc csa, I can't find a way to do that because I can't match the 10A curve for circuit breaker and get a value for t !?
What's the role of the declared prospective fault current - 50kA?
Do I have to use that formula to calculate disconnection time or use figures from appendix 3?
PS: Here is the beginning of my calculations!
I'm doing C&G 2357 and hopefully one day I'll become good electrician like you all.
I'm currently doing my 304 home assignment and I'm a bit confused.
I have to find min csa of live conductors for current-carrying capacity and voltage drop for 5kW, 400V three-phase machine. Ambient temperature - 20[SUP]o[/SUP]C.
- So I find I[SUB]b[/SUB] = P / (√3 x V) = 5000 / (√3 x 400) = 7,2 A
- then choose for I[SUB]n[/SUB] = 10 A ; choose 10A BS EN 60898 - type D ; Reference method B
- Correction factors: C[SUB]a[/SUB] = 1,03 ; C[SUB]g[/SUB] = 0,65*
- I[SUB]t[/SUB] => I[SUB]n[/SUB] / (C[SUB]a[/SUB] x C[SUB]g[/SUB]) => 14,93 A
- choose cable with csa 1,5mm[SUP]2[/SUP] and I[SUB]t[/SUB] = 18,5 A
- check voltage drop - Vc = (mV x I[SUB]b[/SUB] x L)/1000 = (29 x 7,2 x 23)/1000 = 4,8 V (L = 23m)
- check for shock risk - Z[SUB]s[/SUB] = Z[SUB]e[/SUB] x R[SUB]1[/SUB] x R[SUB]2[/SUB] ; R[SUB]1[/SUB] x R[SUB]2[/SUB] = 30,20 x 23 x 1,02 = 0,708 (1,5mm[SUP]2[/SUP]/1mm[SUP]2[/SUP] cpc)
* I'm confused for the grouping factor as well. There's a note under table 4C1 saying the table can be used only for equal loads. In my task there are 4 different loads! Can I still use that table to give a vale to my grouping factor
Thank you in advance