dgrande

I understand that the formula to work out a 3 phase current is
I= P/(1.732 * V * pf)

I have a 3 PH+N water pump rated at 4kw, so

I= 4000/ (1.732 x 400 x 0.8)

I= 4000/554.24

I= 7.21 Amps per phase

The problem I have is that the label on the pump control says that its rated current is 40Amps, Have I missed something?
thanks
 

Attachments

  • [ElectriciansForums.net] Calculating 3 phase current
    IMG_3886.jpg
    249.5 KB · Views: 130
Also lock rotor LRA I suppose but it makes no sense to me why they'd state that as a rating and not the run current and maybe the max Icu of the internal components in kA.
 
Always take notice of the electrical data label on the motor, NOT on the panel controlling the motor!! That panel could be a manufacturers standard panel, that covers many of it's pump/motor sizes etc!!
 
Last edited by a moderator:
As above always go on the name plate of the pump/motor . I have been on many a brake down in factories arguing with people who have connected a motor wrong ie- star/delta and all they will say is the last one was connected that way so I just copied connection's. Doesn't matter just refer to the nameplate for everything to do with motor you are working on that goes for connections, contactor's, overloads etc.
 

Reply to Calculating 3 phase current in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

Similar threads

I got this all wired in and working thanks to the help from James, absolutely top man. Do have a small issue with current imbalance atm, L3...
Replies
10
Views
2K
I have sent you my contact details where in the West Midlands are you? I am based north of coventry but travel the county and beyond you may...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top