a local pub i do alot of work for wants to build 6 pod style holiday lets in its beer garden and has applied to western power to see if the existing supply can cope with the demand
the existing supply is 2 phase with a 200 amp fuse in each phase leading to a busbar system. ive been asked to calculate for the owner what the maximim demand for these 6 pods will be in total
hes given me the following info
Building requirement: 7.5kw
3.5kw Space Heating
3kw Water Boiler
1kw Lights (LEDs)
Appliance requirement: 8.0kw
1kw Microwave
1.5kw Kettle
3kw Oven
0.5kw TV
1kw Hair Dryer
1kw Iron
for me i'd of said the heater and water boiler are likely to be on at the same time and maybe an appliance or 2 so i'd allow 8kw per pod but 8x6 pods would be 48kw? can i apply any further diversity or is that the figure i'll have to give??
many thanks rob