I have a problem. It's calculating inverter for 3 pharse non-synchronous. I mean that i don't know the formula. My colleagues show
Here we go :
P[SUB]1[/SUB]/P[SUB]2[/SUB] = (n[SUB]1[/SUB]/n[SUB]2[/SUB])[SUP]3

[/SUP]Please help me out
Thanks
 
Dear All,
I have a problem. It's calculating inverter for 3 pharse non-synchronous. I mean that i don't know the formula. My colleagues show
Here we go :
P[SUB]1[/SUB]/P[SUB]2[/SUB] = (n[SUB]1[/SUB]/n[SUB]2[/SUB])[SUP]3


[/SUP]Please help me out
Thanks

Rate the inverter for the motor being used.
It really is that simple.
 
The only real effect on a drive with cable length is if it needs line filters for EMC compliance. Otherwise as Besoeker has stated, match the dive for the motor size.

Most drives will have 2 ratings heavy duty and normal duty, pick which is suitable.

Cable size is then specified using the normal methods.
 
The only real effect on a drive with cable length is if it needs line filters for EMC compliance. Otherwise as Besoeker has stated, match the dive for the motor size.

Most drives will have 2 ratings heavy duty and normal duty, pick which is suitable.

Cable size is then specified using the normal methods.

Currently commissioning an MCC fitted with ABB ACS 800 drives, some of which ABB oversized wrt motor rating plate because of long cable runs.
 
Motors with excessive torque demand on ramping start/stop set-ups may require larger inverters to avoid shock load tripping issues, I know 2 brands that recommend this, also excessive start/stop duty may warrant a larger inverter too.

2 reasons off the top of my head for getting larger inverters than motor rating.
 
Occasionally our choice of inverter will be driven by a requirement for a wider range of carrier frequencies than normal.

Frequency of stop/start cycling would be an issue that we'd address with uprated forced ventilation rather than oversizing.
 
Don't understand how you would get excessive start up current with a correctly designed and set up system.

Not saying you cannot, but just cannot see it in my experience of moving heavy loads with VSD's.
 

Reply to Calculating inverter for motor in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
327
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
303
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
365

Similar threads

Do you have a test meter of any kind? if so, disconnect all four wires that go into the motor and check for a low resistance between them. You...
Replies
1
Views
161
Hi all. OK... Let me just try and clear a 1" square space on the screen inbetween all the highly intrusive ads.... On a site (NHS in fact) and...
Replies
0
Views
374

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top