Tried chokes, they didn't make an appreciable difference.
Appreciable difference to what exactly? What problem were you trying to fix?
If it's charging currents that are deemed to be the problem, and that's not an uncommon problem with PWM inverters, the fast switching edges that cause it are there regardless of the inverter rating. Oversizing the inverter won't change that.
You know the i=Cdv/dt thing.
Here's a measurement I took on a system where the fast edges were causing untimely motor failures:
The major divisions on the horizontal axis are at 2us intervals and the minor ones at 0.4us.
We are currently in the build process of a couple of VSDs that have a 300m cable run. We had the option of going for du/dt filters or sine wave filters. There was a significant cost difference which of course we highlighted. The customer opted for the latter.
In both the real life examples I have given, an increase in drive rating was never a consideration as a fix for cable length.
In fact, in my fairly long experience, it never has been.
But, as ever, I'm prepared to learn even if I am beyond my sell-by date.