J

jamesBoater

i am just a little unsure if i need to use 5 seconds as my D/T or 0.4? PFC obtained through Ze test at origin.

i have been told 2 different answers and any guidance would be helpful.

thanks james
 
On TN systems the maximum permissable disconnection times are 0.4s for final circuits up to and including 32A. 5s for distribution circuits and final circuits over 32A.

For TT systems it is 0.2s and 1s respectively.

If you are trying to work out the 't' in an adiabatic equation then you should be using manufacturers data or at worst the regs book and the time current graphs to tell you what the D/T will be for the OCPD when exposed to the PEFC you have measured. Using 0.4 or 5s for your calculations will more often than not give you an earthing conductor size which is far higher than required.
 
Last edited:
You need to work out the 'S' in the adiabatic for the size of your conductor, not t, you cant work out the 't' as this is determined by the maximum disconnection time allowed for the particular circuit, 0.1, 0.4 etc etc and is a constant.
 
no. t is the time the ocpd takes to trip with the pfc that you have measured. usually be 0.1sec. taken from appendix3 BGB. time/current curves.
 
its the fault current squared X the disconnection time (0.4 or 5 sec)...apply the square route to that sum then divide the result by the factor of K....which for copper is 115
. nope, glenn. get the value of t from time/current curves, and k is 143 if it's a single cable like as wot a main earth is.
 
Telex and D are right here. You have to work out using the graphs/manufacture data, the actual time in which it takes the over current protective device to disconnect the current that would flow in the circuit during fault conditions. (PFC) so if the pfc was lower it would take longer to disconnect! And vice versa! Hope this helps!!
 
Telex and D are right here. You have to work out using the graphs/manufacture data, the actual time in which it takes the over current protective device to disconnect the current that would flow in the circuit during fault conditions. (PFC) so if the pfc was lower it would take longer to disconnect! And vice versa! Hope this helps!!
i`m aware of disconnection times....
 

Reply to calculating main earth size in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
950
I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic
Replies
3
Views
932

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top