My question is on calculating the total load allowed on different main tail sizes. I have asked my colleagues and fellow students the same question, and got different answers. What is your opinon, do you follow the regs to the book by calculating the total current demand and apply diversity? Or just put the new circuits in?
I cant get my head round it as we are only starting to cover design in l3 2330.
The question is say you have a 60a cut out, 16 mm tails. Current board has 2 x 32a shower, ring, 1x16 Boiler,2x6 amp. If you wanted to add 3 x 32a , ring,Hob, double cooker and 1x6amp lighting.
Some one at college said just install it all on a big board the hrc fuse could take it applying diversity for a long time if it ever was all on at the same time?
Some one at work disagreed and said upgrade the supply?
What is your opinon from your experience?
Looking at table 6d1 in the osg the total demand in 87amps for 16mm clipped direct.
If you did upgrade what is the usual price to upgrade to a 25mm supply?
Thanks any help would be great as I cant get my head round the theory of diversity and the realistic day to day use of it. Cheersss!!!
I cant get my head round it as we are only starting to cover design in l3 2330.
The question is say you have a 60a cut out, 16 mm tails. Current board has 2 x 32a shower, ring, 1x16 Boiler,2x6 amp. If you wanted to add 3 x 32a , ring,Hob, double cooker and 1x6amp lighting.
Some one at college said just install it all on a big board the hrc fuse could take it applying diversity for a long time if it ever was all on at the same time?
Some one at work disagreed and said upgrade the supply?
What is your opinon from your experience?
Looking at table 6d1 in the osg the total demand in 87amps for 16mm clipped direct.
If you did upgrade what is the usual price to upgrade to a 25mm supply?
Thanks any help would be great as I cant get my head round the theory of diversity and the realistic day to day use of it. Cheersss!!!